Fotek PID + Artisan Scope #594

Answered by roasterdave
erestrepo12 asked this question in Q&A
Discussion options

You must be logged in to vote

The datasheet for the Fotek MT series controllers indicates that it supports RS-485 communication but the communication protocol described is not MODBUS. It appears to be a custom protocol. A datasheet for the MT series from 2002 shows the same custom protocol. Curious how you confirmed the MT-72 supports MODBUS RTU?

Without MODBUS support you need to write a script to implement this custom protocol to connect the MT-72 to Artisan. Adding this protocol to Artisan is not on the roadmap, sorry.

If you are able to find one, the Fotek NT series controllers do show support of the MODBUS protocol over RS-485. These controllers, or any controller supporting MODBUS should work directly with Artisan.